AC ground problem
Feb 14, 2009 at 11:04 AM Thread Starter Post #1 of 12

indikator

100+ Head-Fier
Joined
Jan 17, 2008
Posts
131
Likes
0
hi sorry for the common question, I am not good in electricity soo articles in the internet confuse me,

so my problem is ground connection is my room wall socket is not really good, it reads 60V and 30V across hot/neutral (i don't know which is which), I suspect that it causes faint hum on the speaker and shock on the computer case,

my best effort to ground it still give a very faint hum (compared to absolute black when I touch the amplifier case), my question is can I replace the AC ground with some megaOhm resistor?

I do not know whether this is ground loop or not, but I have checked resistance across some main component ground and it reads near zero
 
Feb 14, 2009 at 2:06 PM Post #2 of 12
You do not state your location and different countries use different voltages and such, but if you are saying you have 60v from Hot to Ground, and 30v from Neutral to Ground, then you have more than a simple problem.

In the USA, Neutral to Ground should be zero volts, Hot to Ground -or- Hot to Neutral should both measure 110v.
 
Feb 14, 2009 at 4:33 PM Post #3 of 12
The shock indicates there's definitely a problem somewhere. The basic strategy to tracking this down is divide and conquer--plugging and unplugging things until you can isolate the problem to one or more components and/or connectors.

First, make sure you're measuring correctly. You need to measure at the outlet itself with the meter set to the ac voltage setting that allows more than the voltage you expect: 110, 220, whatever it is by you. (e.g. On my meter it would be the 300vac setting.) Make sure you're not trying to measure DC voltage.

As you connect and remove components, the test should always be the same. Always measure the same way at the same outlet and touch the computer to check for shock. Be careful when you touch the computer. Typically is these situations, the current is too small to hurt you, and any damage will be collateral from you jumping and dropping stuff. Just tap it while you have good balance and don't hold anything or touch anything else.

The obvious suspect is the computer itself, so unplug it (and all peripherals connected to it) and check the outlet voltage again. Compare the voltage with and without the computer plugged in. If the voltage is normal with the computer unplugged, the problem is in or connected to the computer. Plug the computer back in but not the peripherals, and disconnect the computer from any powered components (printers, speakers, LAN cables, etc.), and measure again. (You may need to disconnect the monitor and measure, since that may be the faulty component.) If the voltage is normal without anything connected to the computer, the problem is in some other component connected to the computer, or in how those components are connected.

At this point, it makes sense to turn to a general approach. The approach is still to isolate the faulty component, but keeping in mind that any wire could be responsible: audio or digital cables, LAN cables, etc. It may also be a ground loop involving more than one component connected through the power line. The basic idea is to keep the computer plugged in and do the measurement/shock test while you plug/unplug other things. If the problem is in the computer only when it's connected to something, the following will still help you isolate the component, but you'll only check the peripherals, not everything on the power line (or at least start with those). The difference is only in which components you unplug and connect.

So the procedure is as follows. Unplug devices from the power one at a time (and disconnect any other wires it has connecting to other devices) and measure until you get a normal voltage again. Do it in thie following order. Start with anything connected to the computer. Then do those components mentioned above. Finally, start unplugging everything else. If you still can't restore the voltage to normal, disconnect everything--including refrigerators, lights, etc. If that doesn't help, get a new meter or ask someone knowledgable to check it with their meter. At that point, call an electrician.

The main suspects for your symptoms are old television sets, old or cheap stereo equipment, radios, powered speakers, and other electronics, especially those with a two prong unpolarized plug--unpolarized plugs have both prongs the same--polarized plugs have one prong wider or longer than the other. If you have anything like that anywhere on the electrical line (not just the outlet, but the line to the main junction box, i.e. all outlets on the same fuse or breaker), turn the plug around and measure again and touch the computer to see if the shock goes away. Do them one at a time. Of course, do the disconnect test first, and if you find the problem goes away when you unplug one of those unpolarized jobs, turn the plug around and test again. Unfortunately, it's not rare for polarized equipment to be wired incorrectly, in which case you need to rewire it or throw it out.

A little background is needed here. There are different types of cases, but in typical consumer audio equipment, a metal case is often connected to ground. The problem is there are different grounds. Equipment with a three prong power plug usually has the case connected to earth ground--the third prong on the plug. Equipment with a two prong plug is usually, but not always, floating. This means the case is connected to the transformer, but the side that's isolated from the power line. Some two prong audio equipment is connected directly to the power return line. The problem is that with an unpolarized plug, there's no way to know which way to plug it in, so the chassis might be hot or neutral. Connect two different pieces of equipment connected like this but plugged in differently, and you develop a voltage across the interconnect. It's literaly shocking! Fortunately, most of this equipment is designed so that the low impedance path for current does the right thing, so there's very little current flowing across the interconnects, and the shock has very little current. Of course, this small current is enough to overwhelm the sound. There's also quite a lot of equipment with polarized plugs that are wired wrong, and end up with a hot chassis. Televisions are a disaster in terms of grounding, but fortunately, the chassis aren't grounded, so you're only in real danger if you open the case, but it can caue all of these problems if you connect one to your stereo. There's also a lot of equipment that uses cheap shortcuts in the power supply that result in failures with similar symptoms. The worst of these is the thermistor (might be an MOV device) that are notorious for being unreliable. This means any piece of cheap equipment (like powered computer speakers or that cheap receiver) can easily fail like this.

One overlooked thing that can cause this is interconnects. If you connect the right (wrong?) types of equipment, especially if one component is one of those unpolarized jobs mentioned above, it can directly connect a hot chassis to a neutral or grounded chassis. Just turning the plug around can sometimes solve this kind of problem. This polarization issue is the main suspect because it will change the line voltage and cause a shock exactly as you describe. The procedure above will work to locate this, but there's one thing more to try. This applies to any devices, because even the best eqipment might develop a fault. There's a chance you have a more complicated scenario involving interconnects, but it's unlikely unless you did something weird like use an unconventional cable with a special grounding scheme--it happens around here because people mix balanced or professional audio equipment with consumer equipment. The other case where you run into this is when equipment develops a fault.

Disconnect any interconnect cables between the computer or stereo and other powered devices and check again to see if you get shocked or if the voltage goes back to normal. After you've gone through the whole unplugging routine, plug in all the peripherals to the power line, but disconnect any interconnects. Start connecting them one at a time and measure again.

You may have more than one device on the line that causes this kind of problem. It's always more difficult to track down multiple problems. Once you find a component that you can connect/disconnect plug/unplug, work backwards unplugging & disconnecting other things to make sure the problem isn't caused by some combination of two connected components. One or more may be faulty.

Make sure you understand the purpose of the procedures before starting or you risk wasting a lot of time. Ask questions before you start.

Once you isolate the problem, you can work on fixing it. That could be even more interesting.

Is this what you have? Type C (European 2-pin) http://www.kropla.com/!c.htm
If so, there's no question of earth ground. That's unpolarized, so you might have to play around with which direction you plug things in. Do you have any equipment with a three prong power plug? If so, how do you connect it?
Finally, if you live where I think you live, you may really just have a low voltage coming from the power company. But 60 is ridiculously low, since that starts at 220vac. The only way to correct it is with a special type of UPS, battery system, or voltage regulator.
 
Feb 16, 2009 at 11:45 AM Post #4 of 12
thanks for the reply,
so I spend my weekend reading many article from SiBurning reply at other threads (thanks dude), and it turns out I was wrong, earthing is not high resistance but in fact a low one.....

still my problem is a little misterious as you guys stated above, my country is 220V, and the plug is Schuko (is it written like this?), I just took another measurement and it reads 215V across live-neutral, 55V and 105V across live/neutral-ground, basing on that looks like there somekind of current leak to the ground isn't it, but even if there current leak one of the socket should reads 215V across ground isn't it? very confusing.......

at first I suspect it is a ground loop because of low frequency hum, so I plug only the amplifier to the wall socket and it still hum, hum only happen to this stax amplifier but shock is on every component I plug in

my best attempt to heal this problem is to ground the extension cord ground connection to a concrete crack in my room, symptoms become much lesser, hum is no longer audible, shock give less bite to finger, but now I can hear a high frequency radio like sound (alien like), I don't know if it is related

so does anyone know what is my problem actually? also for information I live in a dorm, different reading on the wall socket in probably due to higher load in the evening right now

edit. also I somehow believe that the reading I took now is strange, I write 60 and 30 before but now I write 55 and 105 (I guess both are left and right but I can't really remember)
 
Feb 16, 2009 at 12:05 PM Post #6 of 12
I really would want to, but I live in a dorm, I feel a bit awkward to be fussy when others have no problem with it
frown.gif
 
Feb 16, 2009 at 12:18 PM Post #7 of 12
Google "ground fault indicator". In the US you can buy a device that plugs into the AC outlet and it lets you know whether there is a problem with the ground wiring. Perhaps you could buy/borrow something similar where you live. If you could show that the ground is indeed wired wrongly, and that this may be a safety hazard, then your school should fix it.
 
Feb 16, 2009 at 12:58 PM Post #10 of 12
By the way, here is one of the ground fault indicator testers I mentioned. This one is for USA 115V use, you should find an appropriate one for your AC mains system. Make sure you use those that are designed for standard AC oulets. There are some which are designed only for use with special AC outlets with GFCI (ground fault circuit interruptor, typically located in bathrooms); unless you have these special outlets you should not use them.
 
Feb 16, 2009 at 3:30 PM Post #11 of 12
Did you reverse the plug? That's the first thing to do. That's a symmetric outlet, which means you can easily reverse hot and neutral. It shouldn't matter, but it often does.

For now, I'd follow the KGB philosophy: trust but verify. Assume the power is wired correctly, but get hold of some tester if you can and make sure. Meanwhile, there may be some things you can do to get rid of that hum and high frequency noise. That might be plain old high frequency noise on the lines. Do you have a power strip with built-in filters?

The 220vac reading between hot and neutral is the only trustworthy number. The other voltage readings don't really tell you anything. See this bulletin by National Electrical Manufacturers Association about Phantom Voltages linked from Home Electrical Testing and Testers. I encourage you to NOT do anything too hands on yourself, for reasons cited in the links below.

There's no way of knowing which is hot and which is neutral without using some kind of tester. You should be able to find the hot lead with a cheap neon lamp tester. It might be helpful to identify which is hot if you plug in things that need to be plugged in one way or the other. The problem is that it's difficult to know which connector was intended to be hot, or if it even matters. It shouldn't matter, but unfortunately, it often does.

You may have a faulty or disconnected ground. Or not. If you can find the appropriate tester, use it on all your outlets. It may be that this outlet isn't grounded properly. It may be that the whole building is wired poorly. My previous apartment had several outlets with hot and neutral reversed. My UPS has a built-in tester that checks that all three leads are wired properly, so I plugged it into every outlet in the house, and just avoided using the bad ones for electronics, power tools, etc.

To test further, you should get hold of a real tester like the one Amb mentioned. I don't know a safe and easy way to test the ground. You'd need to measure the resistance between the outlet's ground and the main physical grounding point at the inlet from the power company, but that's not something you can really do yourself. The resistance should be small, like below 2 ohms.

Here's some more background. I can't find a good article explaining how wiring of consumer products has been mishandled over the years. You'll have to read between the lines and do some more hunting on your own. Again, I encourage you to NOT do anything hands on yourself. 220vac is deadly.
Schuko @ Wikipedia
AC power plugs and sockets @ Wikipedia
AC power plugs and sockets - Polarised plugs section opinionated? @ Wikipedia Note how this article isn't even part of a normal topic page.
This explains why a hot and neutral exist: ELECTRICAL GROUND: Why Three Prongs?
Here's another article that explains how and when you can get shocked, and why a little knowledge is a dangerous thing: Shock current path : ELECTRICAL SAFETY
 
Feb 16, 2009 at 4:31 PM Post #12 of 12
This is basically what I'm trying to say:
Troubleshooting Residential Electrical Problems - a DIY Strategy

It's not necessarily the wiring. It could be, but it's as likely caused by what's plugged into it.

Maybe you could swap the offending component to another outlet and plug other things into this one and see what happens.
 